DRAG DROP
A recent power Outage caused email services to go down. A sever administrator also received alerts from the datacenter’s UPS. After some investigation, the server administrator learned that each POU was rated at a maximum Of 12A.
INSTRUCTIONS
Ensure power redundancy is implemented throughout each rack and UPS alarms are resolved. Ensure the maximum potential PDU consumption does not exceed 80% or 9.6A).
a. PDU selections must be changed using the pencil icon.
b. VM Hosts 1 and 2 and Mail Relay can be moved between racks.
c. Certain devices contain additional details

I don’t think VM Host 2 should be paired with Mail Relay here. If you put both VM Hosts together, it risks blowing past 9.6A on one rack, which kills redundancy and could set off UPS alarms. The better split is VM Host 1 to Target 1, Mail Relay to Target 2. Keeps both racks balanced and under the threshold. Anyone see a reason to choose the other VM Host?