1. NFPA 13, Standard for the Installation of Sprinkler Systems (2022 Edition).
Section 20.15.2.2.1: "Where high-expansion foam is used in combination with sprinklers... Sprinklers shall be designed to provide a minimum density of 0.2 gpm/ft² (8.1 mm/min) over the most hydraulically remote 2500 ft² (232 m²)." This directly supports the 2,500 ft² design area and establishes the minimum density, making 0.225 gpm/ft² an acceptable design.
2. NFPA 11, Standard for Low-, Medium-, and High-Expansion Foam (2021 Edition).
Section 7.6.2.2: "Where the listings for the foam concentrate and the foam-generating equipment do not state a minimum sprinkler design density, the sprinkler system shall be designed to provide a minimum density of 0.20 gpm/ft² (8.1 mm/min) over the foam-protected area." This corroborates the minimum density requirement found in NFPA 13.