1. NFPA 13, Standard for the Installation of Sprinkler Systems (2022 Edition).
Section 9.3.4.1.2: "Horizontal sidewall sprinklers shall be permitted to be located 6 in. to 12 in. (150 mm to 300 mm) below noncombustible or limited-combustible ceilings where listed for such use." This section directly states the allowable range, with 12 in. being the maximum.
2. NFPA 13, Handbook for the Standard for the Installation of Sprinkler Systems (2019 Edition).
Exhibit 9.15: This exhibit and the accompanying text for Section 9.3.5.1.2 explain that certain listed horizontal sidewall sprinklers have been tested and proven effective at greater distances (up to 12 in.) from noncombustible ceilings, allowing for this specific installation parameter.
3. Oklahoma State University, College of Engineering, Architecture and Technology. Fire Protection & Safety Engineering Technology Course FST 3333 - Fire Sprinkler Systems.
Module on Sprinkler Installation Requirements: Course materials covering NFPA 13 sprinkler positioning rules detail the specific exceptions for sidewall sprinklers, including the 6 in. to 12 in. placement rule below non-combustible ceilings when using sprinklers listed for that purpose.