1. NFPA 20, Standard for the Installation of Stationary Pumps for Fire Protection, 2022 Edition.
Section 4.10.2.1: "A centrifugal fire pump for fire protection shall be selected to furnish not less than 150 percent of rated capacity at not less than 65 percent of total rated head."
2. Isman, K. E. (2017). Fire Protection Hydraulics and Water Supply Analysis (3rd ed.). Fire Protection Publications, Oklahoma State University.
Chapter 10, Fire Pumps, Page 318: "The NFPA 20 standard requires that all fire pumps have a characteristic curve with three specific points. ... The third point is at 150 percent of the rated flow. At this point, the pump must be able to produce at least 65 percent of the rated pressure."
3. SFPE Handbook of Fire Protection Engineering (5th ed.). (2016). Springer.
Chapter 21, Water-Based Fire Protection System Design, Section 21.5.2.1, Pump Characteristics: "NFPA 20 requires that the pump characteristic curve have a shape such that at 150 % of rated flow, the head is at least 65 % of rated head." (DOI: https://doi.org/10.1007/978-1-4939-2562-421)