1. NFPA 20, Standard for the Installation of Stationary Pumps for Fire Protection, 2022 Edition.
Section 14.2.6.1.3: "The pressure maintenance pump shall be set to stop at a pressure at least 10 psi (0.7 bar) higher than the pressure maintenance pump start point and also at a pressure at least 10 psi (0.7 bar) higher than the fire pump start point."
2. NFPA 20, Stationary Fire Pumps Handbook, 2019 Edition.
Chapter 14, Exhibit 14.11: This exhibit and accompanying text explain the pressure settings for fire pumps and jockey pumps, illustrating that the jockey pump stop pressure must be at least 10 psi above its start pressure to create a proper operating differential.
3. Oklahoma State University, School of Fire Protection and Safety Engineering Technology.
Course FST 4333, Fire Pumps: Course materials covering fire pump arrangements and control logic emphasize adherence to NFPA 20 pressure setting requirements, including the minimum 10 psi differential between the jockey pump's start and stop points.