1. NFPA 13, Standard for the Installation of Sprinkler Systems, 2019 Edition.
Table 16.2.1.3.1, "CMDA Sprinkler Protection Criteria for Single-, Double-, and Multiple-Row Racks for Class I Through Class IV Commodities Stored up to 20 ft (6.1 m) in Height." This table explicitly lists a required density of 0.30 gpm/ft² over a 2000 ft² area for Class IV commodities.
Section A.3.9.2.8, Rack. The annex commentary clarifies the distinction between shelf and rack storage, noting that shelving arrangements that create flue spaces, such as back-to-back shelves without solid backing, should be protected as racks.
2. SFPE, The SFPE Handbook of Fire Protection Engineering, 5th Edition.
Chapter 41, "Automatic Sprinkler System Design," Section 41.6.3.2, "Control Mode Density Area (CMDA) Design for Storage." This section discusses how storage configuration, including the presence of flue spaces in rack-like arrangements, dictates the selection of the appropriate design density from NFPA 13 tables. It reinforces that configurations mimicking racks require rack storage protection criteria. (DOI: https://doi.org/10.1007/978-1-4939-2565-041)