1. NFPA 13D, Standard for the Installation of Sprinkler Systems in One- and Two-Family Dwellings and Manufactured Homes, 2022 Edition.
Section 8.1.1: "The system shall provide a discharge of not less than 18 gpm (68 L/min) to any single operating sprinkler and not less than 13 gpm (49 L/min) per sprinkler to the two most hydraulically demanding sprinklers."
Section 11.2.2.2: "The number of design sprinklers shall be the one or two sprinklers that are the most hydraulically demanding, as identified in accordance with Section 8.1."
2. SFPE Handbook of Fire Protection Engineering, 5th Edition.
Chapter 21, "Automatic Sprinkler System Calculations," Section 21.5.3, "Residential Sprinkler Systems." This section explains that for NFPA 13D systems, the water supply must satisfy the greater of the two conditions (one sprinkler at 18 gpm or two at 13 gpm each). It clarifies that the two-sprinkler calculation, requiring 26 gpm, is typically the governing design criterion. (DOI: 10.1007/978-1-4939-2562-421)
3. Oklahoma State University, Fire Protection & Safety Engineering Technology Program Courseware (FST 3333 - Fire Sprinkler Systems).
Module on Residential Sprinkler Design: Course materials consistently emphasize that NFPA 13D hydraulic calculations must be based on the more demanding scenario, which is the operation of the two most remote sprinklers, each discharging a minimum of 13 gpm.