1. NFPA 13, Standard for the Installation of Sprinkler Systems (2022 Edition). Section A.4.3.2, Table A.4.3.2, "Examples of Occupancies for Hazard Classifications," explicitly lists "Offices" under Light Hazard Occupancies.
2. NFPA 13, Standard for the Installation of Sprinkler Systems (2022 Edition). Section 7.2.3.1 states that CMSA sprinklers "shall be installed in accordance with the requirements of Chapters 20 through 25," which cover storage occupancies. This precludes their use in a light hazard office.
3. NFPA 13, Standard for the Installation of Sprinkler Systems (2022 Edition). Section 7.2.4.1 limits the use of residential sprinklers to dwelling units, making them unsuitable for a commercial office.
4. NFPA 13, Standard for the Installation of Sprinkler Systems (2022 Edition). Section 9.4.2.1 generally permits the use of standard-response sprinklers in all occupancy classifications unless other requirements apply. While Section 9.4.2.2 requires quick-response sprinklers for new light hazard occupancies, the standard-response spray sprinkler is the only fundamentally correct sprinkler type for this application among the choices.