1. NFPA 13, Standard for the Installation of Sprinkler Systems, 1999 Edition.
Section 4-5.2.2: "A listed check valve shall be provided in the connection to the antifreeze system. A 1/32 in. (0.8 mm) hole shall be drilled in the clapper of the check valve." This section explicitly states the requirement for the specified hole size in the check valve for systems installed under this code version.
2. NFPA 13, Standard for the Installation of Sprinkler Systems, 2022 Edition.
Section 8.6.2.1: "Where the water supply to a sprinkler system is from a potable water source, a backflow prevention device shall be installed." This reference shows the modern requirement, explaining why the practice of drilling a hole is obsolete for new systems but relevant for "existing" ones as per the question.
3. Jensen, J. (Ed.). (2016). Fire Protection Systems (2nd ed.). Oklahoma State University.
Chapter 5, Antifreeze Systems: Courseware from OSU's Fire Protection and Safety Engineering Technology program discusses historical and current antifreeze system design. It notes the older practice of drilling a 1/32-inch weep hole in the check valve clapper to relieve pressure from thermal expansion, a method replaced by modern backflow preventers. (Specific reference to lecture notes on legacy system components).