1. NFPA 72, National Fire Alarm and Signaling Code, 2022 Edition.
Section 21.3.6: "When ambient conditions prohibit the installation of smoke detectors, other approved automatic fire detectors (e.g., heat detectors) shall be permitted to be installed." This section directly supports the use of heat detectors as an alternative.
Section 21.3.5: This section establishes the primary requirement for smoke detectors in elevator lobbies, machine rooms, and hoistways, setting the context for the alternative mentioned in 21.3.6.
2. SFPE, Handbook of Fire Protection Engineering, 5th Edition.
Chapter 53, "Emergency Movement of Elevators," Section 53.4.2, "Initiating Devices": This section discusses the initiation of Phase I recall, stating, "The initiating devices for Phase I Emergency Recall Operation are required in each elevator lobby... and in the elevator machine room... The code requires smoke detectors to be used as the initiating devices, but it permits other types of automatic fire detectors to be used where smoke detectors are not suitable for the environment." (p. 1938).