1. NFPA 72, National Fire Alarm and Signaling Code (2022 Edition). Chapter 17, Initiating Devices, Section 17.6.3.1.1.1 states: "The distance between smoke detectors shall not exceed a nominal spacing of 30 ft (9.1 m)..." This section explicitly establishes the 30 ft nominal spacing as the fundamental rule for smooth ceilings in the absence of a specific performance-based design.
2. SFPE Handbook of Fire Protection Engineering (5th Edition). Chapter 51, "Detection of Fires and Special Hazards," Section 51.5.2, "Spacing and Location of Spot-Type Smoke Detectors." This section discusses the prescriptive requirements of NFPA 72, stating, "For smooth ceilings, the distance between adjacent smoke detectors is not to exceed a nominal spacing of 9.1 m (30 ft)." (DOI: 10.1007/978-1-4939-2565-051).
3. University of Maryland, Department of Fire Protection Engineering. Course materials for ENFP 411: Fire Alarm and Detection Systems. Lecture notes on "Initiating Devices" consistently reference NFPA 72, Chapter 17, to establish the 30 ft (9.1 m) nominal spacing for spot-type smoke detectors as a foundational principle for system design on smooth ceilings.