1. NFPA 13, Standard for the Installation of Sprinkler Systems (2022 Edition).
Section 27.2.1.2: "Where the maximum system pressure exceeds 150 psi (10.3 bar), the system shall be tested at a pressure of 50 psi (3.4 bar) in excess of the maximum system pressure and shall maintain that pressure without loss for 2 hours."
2. Cote, A. E. (Ed.). (2023). Fire Protection Handbook (21st ed.). National Fire Protection Association.
Volume 2, Chapter 8-2, Section: Acceptance Testing of Sprinkler Systems, Page 8-38: "The system is hydrostatically tested for 2 hours at 200 psi (13.8 bar) or at 50 psi (3.4 bar) in excess of the maximum static pressure when static pressure is in excess of 150 psi (10.3 bar)." This section directly supports the calculation for the given scenario.
3. Oklahoma State University, College of Engineering, Architecture and Technology. FST 3333: Water Based Fire Protection Systems.
Course Module: Sprinkler System Acceptance Testing: Course materials specify that hydrostatic testing follows NFPA 13 requirements, stating that systems with a maximum pressure over 150 psi are tested at 50 psi above that maximum pressure.