When the window area exceeds the maximum exposed area specified for fire-rated glass, it is
necessary to split the window into sections that comply with the fire rating requirements. This means
creating smaller sections that are each within the 3 sqm/32 sqft limit and using fire-rated frames to
ensure that the entire assembly meets fire safety standards. This approach maintains the fire-rated
integrity of the glass, while allowing for larger window areas.
Detailed Explanation:
Fire-rated glass is designed to contain fire and prevent it from spreading. If the window exceeds the
maximum exposed area defined by the supplier, the integrity of the fire-rated glass could be
compromised. By dividing the window into compliant sections with fire-rated frames, you ensure
that each pane performs as intended in the event of a fire. Fire-rated frames help maintain the fire
resistance across the entire assembly, making this option the best for safety and compliance.
EPI Data Center Specialist Reference:
EPI recommends adhering strictly to fire safety standards, especially when using materials like fire-
rated glass. The guidelines emphasize that modifications should always respect the manufacturer’s
specifications to ensure the system remains effective in containing and preventing the spread of fire.